Status Planned
Portfolio area Enterprise SCADA HMI
Created by Jake Hawkes
Created on Jun 16, 2023
Alarm Summary display should have a safer mechanism to acknowledge alarms to assure the correct alarm is being acknowledged
http://tcjira.aveva.com/browse/PMFR-479 is the latest ask. This has been requested many times
Expectation
The expectation is that the chance of acknowledging the wrong alarm should be minimalized.
One solution to this would be a two-step process. The first step would be to request acknowledgment by clicking on the alarm. In the second step, a confirmation window would appear. This window would identify the alarm and allow the controller to confirm alarm acknowledgment or cancel the request. The window would have to operate for both point and system alarms.
We might even need to consider that this is needed for certain classes of points (e.g. 'safety-related', a term that is being used specifically in the midstream control rooms of our customer base, as well as the regulator), and/or certain severities, and/or certain alarm types (i.e. HIHI, but not RTN).
It would be expected that many customers would not like a 2-step process particularly since their controllers are already used to current behavior. We'd therefore have to make the two-step process user-selectable.
Idea business value
Minimising accidental alarm acknowledgements is important as these ack's are auditable activities that reflect on the capability of the operator to properly respond to the alarm.
Idea Type Innovation
Work in
OASYSHMI-241 [HMI 2027] Enable Two-Click alarm acknowledgement from Alarm Summary table
Work status
  • Daniel Scarberry
    Jun 4, 2025
    Totally agree. This is the solution and easy to program
    10 years ago, we implemented a two-step alarm acknowledgement process and all controllers quickly adapted to it as they recognized the value of not inadvertently acknowledging the wrong alarm when you are busy, that then disappears.
    How it works. Acknowledging the alarm in the alarm bar clears the alarm and then the pop up comes up as a reminder of what you just acknowledged. The pop-up stays on the screen until acknowledged. The pop-up can display info like an 8-hr. graph, recent events and even a button that classifies the alarm as a false alarm, critical for complying with 192.631/195.446(e)(2). Once you are done with the alarm, then clear the pop up. See the sample image.
    The business value is eliminating accidental alarm acknowledgement which can and does lead to failure to investigate, outages and safety issues. An additional benefit is documenting the delta between the time the alarm is received, alarm is acknowledged, and the alarm is finished. Great data for workload studies required by 192.631/195.446(e)(5).
1 MERGED
Expand alarm annotation and consider a double-ack
Merged
Initial use-case: classifying alarms for future analysis and reporting. e.g. MAOP alarms, false alarms, Safety or DOT related. Eventual use-case: Machine Learning algos take advantage of human classification Also consider this as how we would doub...
Jake Hawkes over 3 years ago in Enterprise SCADA Server Planned